Problem: My furnace's ignitor does not glow? This could be a pressure switch, limit, roll out switch, or furnace control board problem.
I see this problem many times during the heating season . When your thermostat calls for heat the draft inducer (please see pictures below) should start which creates a draft in your vent pipe. If your vent piping is open and your pressure switch is working properly the pressure switch will close the connection between two wires and send a signal to the control board saying, "Yes it is OK to continue with the ignition process."
Also, all of your limit controls and other safety devices must be closed (a closed circuit between the two connections) to allow the furnace ignitor to glow and start the ignition process. If there is a break down in the pressure switch or other limit safety controls the furnace, for your safety, will not proceed with the ignition sequence. The computer chip inside the board says, Wooooh, something is wrong here! Most furnaces will try this sequence for a total of three times then lock out. On most furnaces the only way to get them out of lock out mode is to turn the switch (looks like a light switch) on the side of the furnace to off and then back on again.