    Default Lennox 78UGF4 blower motor question

    Model Number: 78UGF4
    Brand: other
    Age: More than 10 years

    I recently replaced a whining and noisy blower motor on my old Lennox furnace, and it's working great, but I just have one question. The old motor had 3 wires coming out of the connector on it. According to the diagram on the old motor, the red wire was plugged into the "med-low" speed setting.

    The new motor has 6 wires of course. The furnace electrical diagram only shows wiring for the black (ac), white(common), and red(heat), it doesn't appear to show any additional wiring for multi speed fan settings.

    So I picked the low speed setting for the heat wire. I am assuming I can configure this thing to use the "medium" blower speed setting on heating the house. (I live up north where it gets cold)

    I will assume that by using the medium speed setting, the fan will be louder, so there is that negative.

    My question is this: Are there any safety factors to think about when using low speed vs medium speed? Or health of the furnace in general? I read a little about measuring the change in temperature between supply side air vs heated air output, but not really sure where to measure that, or maybe my question for that is how do the pros measure that.

    -Jerry

  2. #2
    Join Date
    Jul 2006
    Location
    Murray, Utah 84107, United States
    Posts
    31,243

    Default

    Quote Originally Posted by JerryIrons View Post
    Are there any safety factors to think about when using low speed vs medium speed?
    No safety issues at all but I'm not sure I'm following you completely. The original motor was set on low-medium speed and you want to set the new motor on medium speed.- That shouldn't be a problem.
    OWNER RICK'S APPLIANCE REPAIR
    APPLIANCE TECHNICIAN FOR 31 YEARS
    REFRIGERATION SPECIALIST
    ONLINE SERV TECH: ApplianceBlog.com
    CERTIFIED TYPE 1; TYPE 2.....REFRIGERATION SERVICE E.S.

  3. #3
    Join Date
    Sep 2012
    Location
    wny
    Posts
    10

    Default

    Yeah that's basically it, I was just worried that by leaving it on low I could cause the furnace to run too hot. I did do a little more digging, and I'm going to measure the change in temperature. I'll drill a small hole in the return air section a little before entering the furnace and measure the temp with a meat thermometer. I have a humidifier attachment so I'll make sure to close that off before measuring. Then I'll drill a small hole in the supply air coming out of the furnace, near the furnace but after the first turn to avoid a radiant heat reading. I found the sticker inside the furnace listing the temperature change range. So after the furnace kicks on and runs for 15 minutes I'll take my two readings and see how it looks. If it's in range I'll just leave it on low. I might even put it on medium just to see how it sounds and works. Cover up those holes with metal tape and call it a day.

    Thank you for your reply, the more I thought about it the more I realized that yeah, putting it on medium would not cause any safety issues like you said, it will only cause the furnace to "run cooler" so to speak.

    -Jerry
    Last edited by JerryIrons; October 30th, 2018 at 10:29 AM.

  4. #4
    Join Date
    Jul 2006
    Location
    Murray, Utah 84107, United States
    Posts
    31,243

    Default

    Keep us posted on your progress
    OWNER RICK'S APPLIANCE REPAIR
    APPLIANCE TECHNICIAN FOR 31 YEARS
    REFRIGERATION SPECIALIST
    ONLINE SERV TECH: ApplianceBlog.com
    CERTIFIED TYPE 1; TYPE 2.....REFRIGERATION SERVICE E.S.

  5. #5
    Join Date
    Sep 2012
    Location
    wny
    Posts
    10

    Default

    Ok, just to follow up, I did some temperature change testing. Sorry about the delay but we had some nicer weather and I didn't really feel like roasting people out of the house haha.

    So, according to my sticker in the furnace, I have a temperature rise range of 35-65 degrees, with a max air outlet temp of 165. I did some closer reading of the documentation that came with the blower motor, and it looks like the red wire is low fan speed, yellow is medium low, and blue is medium. (when plugged into H for heat on the control board)
    Just as a side note, I have a register not too far downstream from the furnace, and the temperature readings there were very close to the two holes I drilled between there and the furnace. (about 1 degree, sometimes 2. Also I drilled two holes because I wasn't sure if I was too close on the first one to pick up radiant heat)

    Anyway, the testing:
    red wire, low fan speed: temperature range of 70 degrees. (high end was 144)
    yellow wire, low med fan speed: range of 64 degrees
    blue wire, med speed: 57 degrees.

    So I went with the blue wire, medium fan speed. It's a little louder, but it's healthier for the furnace. I probably could run it on low even though it's a 70 degree difference, since it's pretty close, but the problem will be in the middle of winter and a furnace filter hasn't been changed in a while, then it's going to run too hot from the reduced air flow.

    Anyway, in case this helps anybody else out, check your temperature range difference, thanks.
    Last edited by JerryIrons; November 13th, 2018 at 01:41 PM.

  6. #6
    Join Date
    Jul 2006
    Location
    Murray, Utah 84107, United States
    Posts
    31,243

    Default

    Thanks for the update!
    OWNER RICK'S APPLIANCE REPAIR
    APPLIANCE TECHNICIAN FOR 31 YEARS
    REFRIGERATION SPECIALIST
    ONLINE SERV TECH: ApplianceBlog.com
    CERTIFIED TYPE 1; TYPE 2.....REFRIGERATION SERVICE E.S.

Similar Threads

  1. Lennox G12 furnace: Blower not coming on
    By pwrsrge220 in forum HVAC
    Replies: 3
    Last Post: January 13th, 2014, 05:03 PM
  2. FIXED: Mystery Blower Motor
    By gingergirl in forum Whirlpool/Roper/Estate
    Replies: 10
    Last Post: April 4th, 2013, 09:53 PM
  3. Blower Motor Oil Ports
    By Krok0504 in forum HVAC
    Replies: 0
    Last Post: December 16th, 2012, 03:33 AM
  4. Quick Question About Blower/Motor Assembly
    By mrejda in forum Sears Kenmore
    Replies: 3
    Last Post: October 11th, 2009, 01:44 PM
  5. Replies: 4
    Last Post: July 16th, 2008, 11:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
If you feel that you have benefited from this site, and would like to show your appreciation, you can throw a buck or two in the Appliance Blog Tip Jar - Thank you!