Frigidaire FPRH19D7LF1 (2014) standalone refrig not chilling below 40-42

dawg11

Premium Member
Joined
Sep 15, 2021
Messages
6
Location
GA
Model Number
FPRH19D7LF1
Brand
Frigidaire
Age
6-10 years
Right at 1 year ago, we had the freezing of items problem I've seen about this unit. I replaced the thermistor. Initially I believe I had a couple of more freezing sessions (so I thought problem still there) but the freezing stopped and refrig has been left at 34 setting. The thermometer I put in there was reading around lower 30's to near 40 depending on when I looked but everything was always good and cold (since last Sept). Now, the last 5 days, it won't go below 40-42. I even tried 33 on the setting to no avail. I see there is another thread on a similar unit, the FPRU19F8FR. I think it might close to the same model/parts.
Do I need to remove back panel inside refrig and look for partial frost like described in that thread? If I see partial frost, does that indicate freon leak? If so, could a valve be brazed in, system vacuumed, and then re-add 134a to appropriate pressure? If I do not see partial frost, check thermistor reading? Could control board be involved? This is a built-in look with a matching freezer. I cannot imagine having to replace it/them. Any help is appreciated.
 

rickgburton

Appliance Tech - Moderator
Staff member
Joined
Jul 11, 2006
Messages
44,782
Location
Murray, Utah 84107, United States
Make sure the condensor is clean and both fans are working first. When you check the frost pattern leave the machine plugged in and running. A partial frost pattern indicates a problem in the sealed system. A refrigerant leak is only one possibility.
 

dawg11

Premium Member
Joined
Sep 15, 2021
Messages
6
Location
GA
So I have a partial frost pattern. The pipes and fins on left have frost. Is freon leak most probable cause? Anything else I should check? I was thinking I would try a BVP31 piercing valve (I assume I don't have a port but haven't looked - going to a pain to pull out) and check low side pressure and add 134a if necessary. This sound reasonable? I suppose everything should be running when I check charge? Should it be 10-15psi? Looking for at least a temporary fix.

20210915_174126.jpg
 

rickgburton

Appliance Tech - Moderator
Staff member
Joined
Jul 11, 2006
Messages
44,782
Location
Murray, Utah 84107, United States
Yes, that's a sealed system problem. It's either a leak. restriction or inefficient compressor. There are no service valves on that machine.
 

dawg11

Premium Member
Joined
Sep 15, 2021
Messages
6
Location
GA
Ok. Should I be getting 10-15psi on low side when I check it? I saw some testing of compressors using ohm meter on youtube. Is that what I should do to test the compressor efficiency? Could a bad defroster cause this or would the frost be more uniform?
 
Last edited:

rickgburton

Appliance Tech - Moderator
Staff member
Joined
Jul 11, 2006
Messages
44,782
Location
Murray, Utah 84107, United States
Should I be getting 10-15psi on low side
No, not even close. Sealed system repairs are best left to the pros. I can't teach sealed system repairs online. The last time I helped someone with a SSR it took up way too much of my time. Over two months and like 100 posts. There's too many variables and some things you just can't teach online. Sorry
 