Hey so my LG window air conditioning unit stopped blowing cold air. It basically only works as a normal fan now. When I switch it to the COOL function, the fan continues to blow, then when the compressor kicks in, it sounds like its working hard, then it just shuts off after a couple of seconds. Then after another 10 seconds or so, it tries to come back on and shuts off again.
Does it sound like I need to change out the compressor?
 

rickgburton

Appliance Tech - Moderator
Staff member
Joined
Jul 11, 2006
Messages
40,307
Location
Murray, Utah 84107, United States
Does it sound like I need to change out the compressor?
That's what it sounds like. How many amps does it draw? I can't get anything to come up with that model number.
 
G

Guest

Guest
Before you condemn the compressor, make sure the condenser coils are clean and the air vents on the sides are not blocked by leaves, dirt, or other debris. Clean the condenser coils with a garden hose by spraying the coils from the back of the air conditioner. Hope that helps!
 

Dan O.

Appliance Tech
Staff member
Joined
Oct 9, 2004
Messages
3,500
Location
Ontario, Canada
Jake W. said:
Clean the condenser coils with a garden hose


That will not do anything to help the compressor run. If they can get it running then they can clean the a/c if needed.

JMO

Dan O.
 
G

Guest

Guest
It sure will. By their description the compressor is running, overheating, and shutting down. A dirty condenser will cause that.
 

Dan O.

Appliance Tech
Staff member
Joined
Oct 9, 2004
Messages
3,500
Location
Ontario, Canada
The OP said, "it just shuts off after a couple of seconds".

It takes a lot longer than a couple seconds for a compressor to overheat from a plugged condenser, 5-10 minutes at least. If the compressor will run for 5 to 15 minutes or more, then cleaning the a/c might be warranted.

There's little use putting in the effort of cleaning if the compressor is faulty.


Dan O.
 
Last edited:

rickgburton

Appliance Tech - Moderator
Staff member
Joined
Jul 11, 2006
Messages
40,307
Location
Murray, Utah 84107, United States
I agree with Dan. If it shuts off after a few seconds of running, condensor is not the problem. Most compressors won't get hot enough to open an overload just from a dirty or blocked condensor. That's why I asked about the amp draw.
 