True TUC-72 commercial/restaurant refrigerator only cooling to approximately 60-65°F. Unit is 1.5yrs old, we noticed when compressor was continuously running.
Compressor is functioning. Condenser fan is operating, condenser coils are clean. Both (2) evaporator fans are operating. Unit has (3) doors and all seals are intact and in good condition, perimeter heater is functioning.
I measured capillary temperature into evaporator of 38-40°F and compressor suction of 68-70°F. Temperature control will turn the compressor off at approximately 60°F, all other settings (2 thru 9) cause it to run continuously.
Any ideas or help would be greatly appreciated. Thanks in advance.